O

Orange

Hi,
My boiler is losing pressure. I cannot not find the filling valve.
Can anyone help, please?

Many thanks!
 

Attachments

  • IMG_5447.jpg
    IMG_5447.jpg
    93.7 KB · Views: 28
Your missing two black levers (like washing machine valves) have you got a set of pliers ?
 
Hi Shaun,
I do. Which part of the boiler should I toucan, please?

Many thanks.
 
Last edited by a moderator:
The flex pipe either end should be a brass tail sticking out (silver valves that the flex is attached to)

There's two flats on the brass tail, inline with the pipe open and shut is across like in your pic

Open the least accessible one first (already might be open hard to see)

Then open the other one slowly once you reach about 1-1.25 bar cold close the valves
 
All sorted ??

Don't forget to close one or both of them :D
 
I'll let you know once I have found the courage to do it. I'm terrible at such jobs :-(
 
Status
Not open for further replies.

Reply to Boiler ALPHA CD28C repressurize in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
110
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
121
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
142
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
249
Hi they used to say as a last resort you could discharge the D2 pipework at high level and turn it back to the wall. Similar to a combi boiler. I have just looked back through the regs this seems to have changed and it isn't mentioned now. It now mentions if at high level it should be discharged...
Replies
11
Views
250
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock