Seeking any input on a matter that seems to defy logic and common sense.

Sealed system Oil fired boiler (newish) feeding a large farmhouse from an annex with a good quality install/ pump etc that seems to be doing the job.
The system is losing 1 bar per day for a long time. I isolated the flow return in the entrance to the house and left for 24 hours, the pressure did not move, so presumed copper pipe leak undergrounds in the concrete.
Then I thought to make sure the flow /return I had isolated fed all the rads in that house, I turned on the heating and low and behold it only isolated 5 rads in the kitchen and utility room area.

I then as a stop-gap before further underground leak exploration I advised that the system would hold the pressure if the 5 rads in the kitchen area were isolated, and that is exactly what happened, the heating was used and the pressure bar did not move whilst the heating was on for the rest of the house.

Spin-on another week and I then was informed that due to extreme cold the isolating valves feeding the kitchen/utility room was being turned on/off just prior and just after the heating was turned on/off.
Now the Bar pressure has not dipped at all, and no top-ups had been carried out? Surely the leak (if that is the issue) would continue with/without the iotation and when flowing again that would shoot the pressure downwards instantly; It hasn’t?


With thanks in advance, can anyone understand why the system is not losing any pressure once the kitchen/utility area isolation valves are opened up and flowing and offer up any scenario that I may be incorrect with my underground leak theory?



Confused.



Many thanks
 
You really need to sketch out the full system ( flow and return paths) to the best of your ability - from what you can see and the information from the tests conducted to date. You have already had one surprise when an isolation did not cut off a set of radiators - there are probably one or two more lurking there too.

If you start off with an indicative plan, all the future tests you do will build up the detail and information in a structured manner. Leak investigation in an adhoc manner is frustrating and does not always deliver results.

Be aware that a leaking pipe encased in screed / concrete does not always leak at a consistent rate - I don’t know why!!

Also worth estimating the volume of water loss that a 1 bar drop on the system leaks - at least then you know what the scale of what you are looking for represents.

Be wary of using a leak detection specialist - never good value for money in my experience
 

Reply to Pressure loss from sealed system stops when open/closing a zone with 'a leak' in the Plumbing Zone area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
209
P
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
141
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
266
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
481
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
260
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock