Discuss How does a boiler sense the condensate pipe is blocked? in the Central Heating Forum area at PlumbersForums.net

Messages
12
How does a boiler sense the condensate pipe is blocked?. Boiler stopped working. I was told the condensate syphon was blocked and had to be cleared. I wondered how the boiler controls knew this?
 
There are sensors in the heat exchanger that are specific to this fault.
They detect the condensate level in the heat exchanger and hence attribute the fault to condensate blockage.

Mind you - 30% of the faults are caused by faulty sensors!!!
 
There are sensors in the heat exchanger that are specific to this fault.
They detect the condensate level in the heat exchanger and hence attribute the fault to condensate blockage.

Mind you - 30% of the faults are caused by faulty sensors!!!
Thanks oz-plumber, I did wonder if perhaps sensor failure could cause the same effect (boiler shutdown/lockout)
[automerge]1587389998[/automerge]
What boiler are we talking about?
Worcester Bosch Greenstar 18Ri.
 
There’s no sensor that I’ve seen they just rely on flame supervision, when the heat ex is full of condensate (or rainwater in some cases) it won’t light and goes into lock out. You can hear the water sloshing around when it’s half full and that’s generally when you get the phone call “my boiler is making a right racket”
Thanks oz-plumber, I did wonder if perhaps sensor failure could cause the same effect (boiler shutdown/lockout)
[automerge]1587389998[/automerge]

Worcester Bosch Greenstar 18Ri.
 
What does? Are you saying an increase in fan pressure correlates to a blocked discharge? That would make sense

how the boiler senses the condy is blocked water will rise back into the hex blocking the flue so the ap switch senses this which in turn turns the boiler off / fault
 
Don’t under any circumstances attempt to by pass the sensor.

To avoid such intervention, most boiler control logic sequences will initially test the APS to be open before fan start up, only firing once the fan has started and subsequently proved the APS closed.

Never override or attempt to override a safety control sequence.

In my business it is a summary dismissal offence.
 
Don’t under any circumstances attempt to by pass the sensor.

To avoid such intervention, most boiler control logic sequences will initially test the APS to be open before fan start up, only firing once the fan has started and subsequently proved the APS closed.

Never override or attempt to override a safety control sequence.

In my business it is a summary dismissal offence.

Agreed Brambles. We had this conversation some time ago 👍
 

Reply to How does a boiler sense the condensate pipe is blocked? in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
142
Recently had a Viessmann Vitodens combi boiler installed, quite often when the adjacent cold mixer tap is opened the boiler starts for a few seconds! Can anyone tell me what is causing this? And how to cure?
Replies
3
Views
196
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
248
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
221
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
229
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock