Hi Folks,

I have a challenge with a Main Eco Elite 30 Combi which is short cycling on the CH. Water works fine. As soon as you have call for heat, the boiler fires up, modulates, but jumps very quickly (about 30 seconds or so from 40'ish all the way to 70, burner disengages putting it the boiler into its 3 min cycle for it only to repeat. Radiators upstairs heat up (moderately but not optimal) with downstairs stone cold. 9 radiators in total.

Was advised originally that a powerflush was required. 2 x full circuit powerflushes, plus a boiler flush on its own. The main heat exchanger was also removed by the engineer and manually flushed, followed by a powerflush directly (as thought it may be blocked)

CH Return flow pipe still does not get up to temp as the short cycling is probably not allowing heat to circulate all the way round the circuit as a result of the short cycling?

The following have already been changed

CH temp sensor
Diverter valve
Pump
DHW plate exchanger
DHW temp sensor

Pretty frustrating as the boiler still short cycles. The interesting thing was when the boiler inlet outlets were connected to the powerflush and boiler switched on, still seemed to short cycle, even with a decent powerflush flow.

The only thing which has not yet been changed is the inlet assembly, could there possibly be a block between that and the main heat exchanger?

Any thoughts please.

PS, yesterday when the DHW engaged, almost felt as hot water was being let off into heating flow pipe, Engineer swapped out replaced diverter for a new one this morning , but it has not resolved the situation.

As a next step, the Engineer is now wanting to do a second powerflush of the boiler alone with some chemicals (ferrnox f2 )and run that for an hour or 2 as he thinks the main exchanger may be scaled up?)

Any thoughts or ideas please....

Al
 
Return filter clean in the valve ?
 
I had a problem like this about 24 years ago on a heating system in a house in Keithley. The boiler was also short circuiting. Three other plumbers had been before and hadn't fixed the problem. I asked what the other guys did so as not to repeat their fault finding. So, what I did was to open all the rad valves to fully open (both sides) then run the boiler with the pump on full. There was an almighty gurgle and banging noise and everything started to work. It was an air (hydrogen) lock. I then rebalanced everything, bled the rads and that was that.

It might be worth a try on your system.
 
I had a problem like this about 24 years ago on a heating system in a house in Keithley. The boiler was also short circuiting. Three other plumbers had been before and hadn't fixed the problem. I asked what the other guys did so as not to repeat their fault finding. So, what I did was to open all the rad valves to fully open (both sides) then run the boiler with the pump on full. There was an almighty gurgle and banging noise and everything started to work. It was an air (hydrogen) lock. I then rebalanced everything, bled the rads and that was that.

It might be worth a try on your system.
Thanks Rplumb, it was the first thing we tried..... but to no avail
 
What kw of rads do you have and 10mm to them or 15mm ?
 

Reply to Eco Elite 30 short cycling on CH in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
145
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
242
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
147
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
354
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
253
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock