Messages
7
Hi all, I think has been discussed before but I don't think I've seen a clear answer. We have the Vaillant boiler as above and the filling loop has started to leak from around the olive joint on the cold water side.

I would like to replace the whole loop, flexi, taps and the valves etc.

I can turn the cold water main off with no problems but my question is, would removing the central heating return side end up draining all the upstairs radiators by removing this valve please?

I can turn off the valve between the TF1 and up to the boiler and I presume the Vaillant has a valve/solenoid to prevent water draining from the boiler down (mains water would be off at stopcock) but would the rads water pressure push water out on that side?

I guess i could just replace the leaking cold water check valve side and leave the rad valve side in place but would like to replace all if poss.

I attach some pictures.

Many thanks!
 

Attachments

  • 1.jpg
    1.jpg
    449.5 KB · Views: 15
  • 3.jpg
    3.jpg
    435.3 KB · Views: 12
  • 2.JPG
    2.JPG
    193.9 KB · Views: 12
If you turn off the the valve above for the fernox omega, then you’ll get a little bit out, but if you keep the loop on that side, disconnect the water side, then you have a makeshift drain hose, place hose into a suitable container and open the heating side, continue with replacement after water has stopped. You shouldn’t get that much.
 
Thanks, we have 4 rads upstairs, would they end up draining through this? How quick would the flow be?

I guess since I am keeping the olives and original nuts in place when I replace the loop I could just be quick to screw the new valve on to the rad return side.

Do you recommend and PTFE as well at the olive side considering they are originals?

Cheers,
Chris
 
Hi Chris,

No it shouldn’t drain upstairs rads. If you use the flexi as I’ve said, you can control the flow, although it shouldn’t be all that much. Yes, re-use of olives will be a case of unscrew and screw new ones on. Ptfe is a preference, but since you want to get it right, it’ll do no harm, just don’t put any on the threads - it’ll look naff and do nothing 😂

Also Chris.
 
Tbh

Loosen the heating side valve enough so you can undo the rest by hand be careful you don’t undo it all the way yet

remove the flexi cold water side and insert into a bucket open the valve

Have the other valve on hand

Wait until you see the pressure drop close the valve undo the nut fully

Then open the valve into the bucket again and quickly pull the old one off and put the new one on

Tighten up and your done the heating side
 
Hi Chris,

No it shouldn’t drain upstairs rads. If you use the flexi as I’ve said, you can control the flow, although it shouldn’t be all that much. Yes, re-use of olives will be a case of unscrew and screw new ones on. Ptfe is a preference, but since you want to get it right, it’ll do no harm, just don’t put any on the threads - it’ll look naff and do nothing 😂

Also Chris.
Thanks very much Undertrained :)
Appreciate your help.
 
Tbh

Loosen the heating side valve enough so you can undo the rest by hand be careful you don’t undo it all the way yet

remove the flexi cold water side and insert into a bucket open the valve

Have the other valve on hand

Wait until you see the pressure drop close the valve undo the nut fully

Then open the valve into the bucket again and quickly pull the old one off and put the new one on

Tighten up and your done the heating side
Cheers ShaunCorbs. Sounds like we know the recommended procedure then. Many thanks.
Chris
 

Reply to Replacing entire filling loop on Vaillant EcoTec Pro 28 in the DIY Plumbing Forum area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
209
P
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
270
Hi all, I'm installing a concrete patio out back. By the wall under the kitchen sink I have an existing P-Trap gully for the grey water from the sink, dishwasher, washing machine etc. When I pour the concrete there won't be any chance to dig it up anymore. From my own research I get the...
Replies
0
Views
133
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
143
I have a green star ten yrs old keeps increasing pressure, feel on off filling valve not working, drain off to recommended, but after few days it's increased whilst cold...is this a regular problem.
Replies
1
Views
149
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock