I have recently had a UFH circuit added to my existing CH/HW system and had a question on performance when UFH and CH are operating at the same time.

My boiler is an Vailliant EcoTec Plus 630 and for a number of years this was running with a CH and HW loop only. Each loop had a 2 port value controlling the flow. All radiators (11 in total) are TRV and the boiler has a manual bypass fitted. I recently discovered that the boiler has an ABV fitted as standard so question the need for an additional bypass valve. Anyway, it has been performing well since 2008.

Recently a UFH loop was installed in the loft and due to space requirements the manifold had to be positioned there also.

The flow to the manifold is the first connection tee'd from the boiler flow pipe and is controlled by a 2 port valve. The return from the manifold is tee'd into the CH flow near the boiler.

The manifold temp is set at 41C and the boiler is set to 60C. The CH and UFH are controlled by separate room thermostats.

When both the CH and UFH are on and the valves open, the UFH will return water much more quickly to the boiler than the CH circuit does as it is a smaller loop. This results in the boiler temp increasing to max temp (60C) very rapidly and then enter into it's cooling cycle. The result is that the CH circuit does not really get up to an adequate temp and the radiators are only partially warm. If I turn off the UFH then all rads will become piping hot in around 45-60 mins.

Can anyone with experience of a similar setup advise on what can be done to even out the flow so that both circuits can operate simultaneously with the correct performance? Should I lower the speed of the UFH pump at the manifold?

Thanks
 
Are you happy that the manifold thermostatic mixing valve (TMV) is working correctly, it shouldn't take it long to reduce the manifold temperature from 60C to 41C, initially, the temperature of the water returning to the boiler should be quite cool. If this was as low as say 25C then boiler might cycle on high dT?, have you noted a high return temperature to the boiler shortly after starting up both together?.

You could reduce the manifold pump setting to minimum and then gradually increase it if the manifold flow/return dT is too high, what setting is the pump on now?.
 
The above is interesting but is showing hydraulic separation necessary under abnormal conditions IMO, if the boiler can run for the few minutes until the TMV reduces the mixing temperature to 41C (OPs case) then the boiler is only supplying 2.76LPM to the UFH (at 60C) and 7.17LPM to the rads which should not be a problem, there could and probably would be a problem supplying the UFH on its own but a by pass between the boiler flow/return could take care of this.

1671576610066.png
 

Reply to CH and UFH performance problem in the Water Underfloor Heating Advice area at PlumbersForums.net

Similar plumbing topics

We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
266
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
149
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
141
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
209
P
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
258
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock