• Welcome to PlumbersLive.com - Please register for free, or login if you have an account here already. We have relaunched the forum with new forum software and a nice new feel to it. Find common questions related to Boilers, Central Heating, Gas Engineering, Water Plumbing, Bathroom and Kitchen Remodeling - all in our forums.

anybody know much about the cylinders with integrated air source heat pumps

No problems just wondered how good they were
The one I thought about (Ariston) had a CoP (coefficient of performance) of 3.0, i.e. 3kW of heating for 1kW of electricity. To compete with gas I needed CoP > 4.0. Another issue was that unless you have its inlet and outlet terminating outside the thermal envelope of your house, you are paying to heat the air it is extracting its 'free' heat from. And you needed a 12 Amp supply electrical supply, and have long reheat times (4.5 hours), etc.

So, I loved the theory, but CoP > 1.0 is the only upside and IMO that's not enough to win if you have a gas supply and have to pay the going rate for grid electricity.
 

snowhead

Esteemed
Plumber
It doesn't qualify for RHI if it's only DHW, has to include Renewable space heating.

 
The concept of recovering unused heat from within the building is excellent - the Ecocent (Earth Save Products) range are the only ones we have fitted. From a financial perspective the payback period is significant (12 to 15 years) for a capital expenditure of £10k plus.

Without eligibility for RHI they only appeal to people who seek renewable energy at any cost.
 

Ric2013

Plumber
The one I thought about (Ariston) had a CoP (coefficient of performance) of 3.0, i.e. 3kW of heating for 1kW of electricity. To compete with gas I needed CoP > 4.0. Another issue was that unless you have its inlet and outlet terminating outside the thermal envelope of your house, you are paying to heat the air it is extracting its 'free' heat from. And you needed a 12 Amp supply electrical supply, and have long reheat times (4.5 hours), etc.

So, I loved the theory, but CoP > 1.0 is the only upside and IMO that's not enough to win if you have a gas supply and have to pay the going rate for grid electricity.
Typical salesman's gumpf. COP of 3.0 at what air temperature and relative humidity? Internal water temperature of what? And so in real-world conditions, what is the COP?
 