I know it's 1mb drop max from meter to appliance.

a) is this with just that one appliance demanding gas?
 
No mate.
Pipework should be sized so that all appliances will only have a max of one mb. When sizing, kW of all are added.
Don't you remember the pipework calc in the gas safe course?
 
No mate.
Pipework should be sized so that all appliances will only have a max of one mb. When sizing, kW of all are added.
Don't you remember the pipework calc in the gas safe course?

Ah yes.. sorry.. my brain is fried today! Forgot you divide the drop by number of appliances!!
 
Do you know 'why' the drop we aim at is 1 mbar Jaydebruyne?

If you know that, you'll always remember why you're going to the trouble.

It will also help with your 'Engineers discretion '
 
Do you know 'why' the drop we aim at is 1 mbar Jaydebruyne?

If you know that, you'll always remember why you're going to the trouble.

It will also help with your 'Engineers discretion '
 
Do you know 'why' the drop we aim at is 1 mbar Jaydebruyne?

If you know that, you'll always remember why you're going to the trouble.

It will also help with your 'Engineers discretion '

I feel like I should but no, I don't :/ why do we aim for a 1mb drop? I thought it was due to safety of appliances and how to tell if pipework was undersized
 
I feel like I should but no, I don't :/ why do we aim for a 1mb drop? I thought it was due to safety of appliances and how to tell if pipework was undersized

It's because in the UK we have a lot of unregulated (pressure) appliances.
e.g. gas fires, wall heaters, hobs etc etc.

These appliances are designed to work on 20mbar (inlet working pressure).

For years, since the changeover to natural gas, we more often than not, had 21mbar at the meter outlet.

Therefore, in order to get the 20mbar at the appliance, we needed to make sure the calcs for pipe size were correct. ( 1 mbar drop).

You don't want too high or to low a pressure on any unregulated appliance.

It is also very important that the unregulated appliances are not effected by appliances sharing the same installation pipe work. ( like your hob on another post, recently).

Hope this helps !
 
It's because in the UK we have a lot of unregulated (pressure) appliances.
e.g. gas fires, wall heaters, hobs etc etc.

These appliances are designed to work on 20mbar (inlet working pressure).

For years, since the changeover to natural gas, we more often than not, had 21mbar at the meter outlet.

Therefore, in order to get the 20mbar at the appliance, we needed to make sure the calcs for pipe size were correct. ( 1 mbar drop).

You don't want too high or to low a pressure on any unregulated appliance.

It is also very important that the unregulated appliances are not effected by appliances sharing the same installation pipe work. ( like your hob on another post, recently).

Hope this helps !

Makes complete sense and this wasn't covered in my gas course!! Cheers Last ;)

So with all appliances on, it shouldn't matter what appliance you test the drop at should it? i.e boiler and hob on and I test drop at boiler. As long as it isn't below (preferably for the unregulated appliances) or above 1 then you're good to go?
 
test all appliances if a test nipple is present, just encase something is undersized further down,

and meter inlet working - permissible working drop = inlet of appliance (about)

normally you can tell by eye once you have a bit of experience (flame picture)
 
test all appliances if a test nipple is present, just encase something is undersized further down,

and meter inlet working - permissible working drop = inlet of appliance (about)

normally you can tell by eye once you have a bit of experience (flame picture)

Yeah I knew their hob wasn't right as flame pic had changed - top of flames on highest burners went yellow..

Sorry.. just need to ask.. so say I cut in a test point under the hob and under the boiler, I should get 1mb drop between them both - so 0.5 each (for arguments sake, I know this 0.5 will be different values depending on length of run, size of pipe etc to each appliance)
 
Yeah I knew their hob wasn't right as flame pic had changed - top of flames on highest burners went yellow..

Sorry.. just need to ask.. so say I cut in a test point under the hob and under the boiler, I should get 1mb drop between them both - so 0.5 each (for arguments sake, I know this 0.5 will be different values depending on length of run, size of pipe etc to each appliance)

Yea all appliances drop = Pipework drop (under 1mbar)
 
Yeah I knew their hob wasn't right as flame pic had changed - top of flames on highest burners went yellow..

Sorry.. just need to ask.. so say I cut in a test point under the hob and under the boiler, I should get 1mb drop between them both - so 0.5 each (for arguments sake, I know this 0.5 will be different values depending on length of run, size of pipe etc to each appliance)


You should ( in domestic, in theory and in a perfect world ), have 1 mb drop between the working pressure at meter outlet and same gas rate working pressure at each appliance inlet.

Test them with and without other appliances running.
 
Last edited:
Status
Not open for further replies.

Reply to Question on gas pressure drop across pipework in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
484
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
150
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
269
Can anyone recommend a decent multi meter, preferably under a 100 pounds. It's for checking boiler components so I don't need a top spec one ....just easy to use and reliable. The fluke 115 looks good but its above my budget. My current socket and see one was great but it's developed a fault.
Replies
7
Views
242
The fittings below are for a mixer bar attached to a self contained shower. i.e not a wall. The attaching screws have snapped. I could get two new brackets, dismantle that existing one and start again or I could try and re attach via those screws, removing the broken ones from the plate and wall...
Replies
1
Views
209
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock