I have been called out to service an Idel Classic NF 80 boiler
wich was not working. When I undone the control box so that it was
hanging on its wiring the boiler started up as it should. so I put the contol
box back in position and then nothing so undone the control box again as
before and the boiler stated working again. So I checcked all the connections and all the wires for continuity and all seems fine but when I
Screw the control box back the boiler fails to start. I have been in contact with technical support and they say it must be a loose connection but I still have not found one. Has anybody had a problem like
this or any idea what it could be.

Thanks Jeff
 
Well if you can not find a loose connection ,it is probably a dry joint on the pcb,remove pcb board and resolder main connection points and relays
Some would say just replace pcb
 
I have been called out to service an Idel Classic NF 80 boiler
wich was not working. When I undone the control box so that it was
hanging on its wiring the boiler started up as it should. so I put the contol
box back in position and then nothing so undone the control box again as
before and the boiler stated working again. So I checcked all the connections and all the wires for continuity and all seems fine but when I
Screw the control box back the boiler fails to start. I have been in contact with technical support and they say it must be a loose connection but I still have not found one. Has anybody had a problem like
this or any idea what it could be.

Thanks Jeff


Had a similar issue with an ideal elan, again pcb flap down it worked fine, pcb flap up it was clicking and clunking, it turned out to be the aps wires, but I changed pcb and harness and it was fine mate
 
Status
Not open for further replies.

Reply to Ideal Classic NF80 problem in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
140
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
265
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
148
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
344
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
140
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock