Search the forum,

Discuss E133 Error Potterton Titanium 24 in the Gas Engineers Forum area at PlumbersForums.net

abc_plumb

Gas Engineer
Messages
106
Hiya fellow gas engineer.
Need some help on this boiler fault.

Went out to this E133 Error on a Potterton Titanium 24 (GC: 47-393-39)

I checked the inlet standing pressure which was at 25mb. Boiler attempts to fire and the pressure drops by 1mb but the gas valve doesn't open. Checked the black gas lead to the gas valve and I was getting
230v between pins (3L) & E
230v between pins (3L) & (4N)
230v between pins (3L) & (1N)

Checked the gas valve coil and resistance was all good.
Checked X3 on the pcb between 1&2 and getting 230v.
I suspected a sticked gas valve so went there today to replace it with a new one and it's the same fault.

I was told that the pcb was replaced for a reconditioned one 5 weeks ago.

I'm leaning towards the pcb but I'm getting the correct voltage at the black plug end that fits into gas valve???

Would appreciate some help on this please.
 
Gas should drop to under 5 mbar eg 1 or two with the gas isolated
 
Hi Shaun

Are you saying I should've tested the gas valve but turning the boiler gas isolation off then tried the firing sequence. From 25mb is should've dropped to 1 or 2mb?
Handy tip for next time.

I did remove the 3/4" nut above the gas valve and I know the gas was not getting through the g/valve.
I'm positive the gas is not getting through, just can't understand why?
 
Hi Shaun

Are you saying I should've tested the gas valve but turning the boiler gas isolation off then tried the firing sequence. From 25mb is should've dropped to 1 or 2mb?
Handy tip for next time.

I did remove the 3/4" nut above the gas valve and I know the gas was not getting through the g/valve.
I'm positive the gas is not getting through, just can't understand why?

Yes proves if the gas valve is opening

If you have power eg 240v on the pins and no drop gas valve (eg with supply isolated)
 
Faulty ?
 
I've put a brand new gas valve yesterday and I'm getting the same fault. I'm thinking the gas plug is not making the contact with the pins to transfer the 230v to the gas valve.

Feel like my clutching at straws, but can't get my head around this one!

Lift the plug slightly so you can check at the terminals
 
Lifted it, wobbled it, squeezed it..... done it all, but nothing.

I mean you can test with a multi meter on the gas valve pins to see if the connection is ok just a thought as well did you remove the bung on the new gas valve they sometimes put them in to save any rubbish going in them while in the box
 

Reply to E133 Error Potterton Titanium 24 in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
481
  • Article
A Plumber Who Worked Illegally Gets A Suspended Sentence After Falsely Claiming To Be Gas Safe Registered. A Plumber in Herefordshire was prosecuted after Hereford Trading Standards Team found that he was falsely claiming to be on the Gas Safe Register when he was not, putting members of the...
Replies
0
Views
177
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
142
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
270
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock