Discuss Cause of spluttering kitchen tap? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Messages
29
Hi,
I have a sealed & pressurized water system (house is around 10 years old) and a few weeks ago, the kitchen sink tap was spluttering quite loudly each time the cold/hot water was turned on elsewhere in the home. Called a local plumber, showed him what was happening and he said the PRV (pressure reducing valve) was faulty and needed replacing. This was replaced and this made a huge difference initially. However a week or so later, the same problem returned but not as bad as before. It happens less frequently and isn't as loud as before. See video here - the spluttering happens at 0:31


Anyway i called a different plumber for a different opinion last week and he couldn't find anything wrong! He did manage to fully open the valve marked below as he said "that was cracked" but the problem still exists. The video above I only made this morning so couldn't show him that at the time. I have arranged for him to come again to investigate further (will show him the above video) but in the meantime, could anyone tell me what is the likely cause of this spluttering? Perhaps the new PRV hasn't been installed properly or is faulty?

Some photos:





Cheers
 
Start with loosing the gate valve ( round red top ) and at the same time get the plumber to change the stop tap for the correct one .
Thanks but which is the red gate valve? One below the PRV or the one just above the hot water cylinder? And is the 'stop tap' the tap which turns on/off the water supply into the home, which is under my kitchen sink?
 
Its above the cylinder, I am not saying thats the problem but its the first thing I would loose , it shouldn’t be there and they are no good with mains pressure. Brass stop tap you marked cracked should be a full bore lever arm .
 
Ok an update. Had someone come over from the second plumbing company again this morning and they sent a different guy this time. I showed him the video, he had a quick look at everything and decided most likely the issue was at the hot water kitchen tap due to its age (around 11 years). He's replaced the valve there and the tap knob seems to turn smoother and so far I haven't had any spluttering...touch wood :)

I asked him about the necessity of the red gate valve, he said its there if you want to switch off the water supply to the hot water cylinder.

Re: brass stop tap which is non-lever type in my home, he said that's perfectly normal in a domestic environment.
 
I asked him about the necessity of the red gate valve, he said its there if you want to switch off the water supply to the hot water cylinder.

Re: brass stop tap which is non-lever type in my home, he said that's perfectly normal in a domestic environment.

Nothing for you to worry about but I disagree with him on the gate valve. As for the stoptap yes its ok ish but the regs say lever arm valve , so disagree again .
I am just a fussy **** lol
 
Nothing for you to worry about but I disagree with him on the gate valve. As for the stoptap yes its ok ish but the regs say lever arm valve , so disagree again .
I am just a fussy **** lol

Lever arm for what mate ?
 
I would be happy with a stop tap never seen a manufacturer/ regs say it must be a lever valve any chance of a screen shot ?
 
A stopcock is fine. Personally I prefer a fullbore lever valve but the Centre brand CentreStore manual I have here says "A stopcock or servicing valve".

Do other manufacturers say different?
 
Its above the cylinder, I am not saying thats the problem but its the first thing I would loose , it shouldn’t be there and they are no good with mains pressure. Brass stop tap you marked cracked should be a full bore lever arm .

Quite right, gate valves are for low pressure mainly
Also, gate valves should be installed on vertical pipes to prevent crud collecting in the bottom well which could prevent it closing
 

Reply to Cause of spluttering kitchen tap? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
83
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
310
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
103
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
4
Views
390
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock