boiler works fine for rads and hot water, but after reaching required temp and shutting off a noise continues .. sounds like a fan or air blower. Sometimes stops in minutes other times hours. sometimes doesn't happen at all
 
Could have a post purge board fitted. Once the burner has finished burning the post purge will run the burner motor to empty the combustion chamber of combustion gases to prevent fumes being pushed back into the property.
 
Post purge most likely, assuming the noise is localised to boiler? What burner is it?

I believe post purge is wired through a PCB in control panel on this boiler.
 
Last edited:
HI both, thanks for the input. It is a Worcester Heatslave 20 /25 and I have taken the lid off and checked that it does have a post purge PCB - which is then connected to the main board

I have found a new post purge board to purchase from a decent supplier - just wondering whether swapping the board is something I can attempt as a DIY job.
 
HI both, thanks for the input. It is a Worcester Heatslave 20 /25 and I have taken the lid off and checked that it does have a post purge PCB - which is then connected to the main board

I have found a new post purge board to purchase from a decent supplier - just wondering whether swapping the board is something I can attempt as a DIY job.

The purge unit should only have a couple strips with wires going to it and fix in place. It should be a simple job providing electrical supply is isolated first. If you're sure you have the right part number and have found the correct replacement you could give it a go, if you don't feel confident then please get an engineer out. Bare in mind there is a couple variations of the post purge units for the heatslave over the years so make sure it is the right part.
I have spoke to my associates with more experience on this unit than myself and most of them agree that these units are more hassle than they're worth and the other option is to link the unit out. I'm not going to say how to do that but it is an option and experienced engineer can undertake it for you should you wish.
 
Thanks again for the clarification. I did think about bypassing the fan but prefer to keep it in use since the boiler has been fine with it for many years.
The part number seems accurate - so I will attempt the swap out of the board let you know how I get on
 
Thanks again for the clarification. I did think about bypassing the fan but prefer to keep it in use since the boiler has been fine with it for many years.
The part number seems accurate - so I will attempt the swap out of the board let you know how I get on


I might be misinterpreting what you're saying but the fan is an important part of the combustion process, pre purge and post purge, plus if the motor and fan weren't energised you'd have no ignition. It should not be linked out all together! Linking the post purge out just stops the fan continuing after the stats have shut the control box and burner down. Your problem is the timed relay on the post purge board, it should run after burner shutdown for a set period of time, yours is acting randomly.
Swap the unit over if you can and let us know, it is a simple straightforward swap, linking out requires more and I'm not going to explain to you how, that's left for an engineer.
 
Last edited:

Reply to Worcester 20 25 heat slave in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi I have a worchester heat slave 18/25 and continually needs bleeding of the Kero, runs all day when bled. when it cuts out on the stat it wont start again without bleeding
Replies
1
Views
124
T
Hello, I have just moved in to a new flat this week and have a problem with noise coming from somewhere around the top of the boiler. It's a loud clicking/knocking sound that lasts about a minute, stops for 20-30 seconds and starts again. It seems to happen at night, starting in the evening...
Replies
1
Views
332
We have this boiler installed and it's started to give issues. The service was done and passed ok. But only as there was no noise for the guy to hear. Radiators are fine. When hot water is being used it generally seems OK, but sometimes there's a large rumble noise 10-15 secs then it stops. I...
Replies
3
Views
414
When I turn on our CH there's a lot of noise from one specific part of the system - the pipes on the landing, and one radiator. It sounds like air, and the landing radiator needs bleeding regularly (about once a month), even though it isn't the highest point in the system. The two upright rads...
Replies
35
Views
1K
Hi there, My boiler (Worcester Greenstar Ri) has started making a soft knocking noise when it turns on, and again a few times when it turns off. I've attached a short video of the sound. It isn't constant, it seems to happen within the first 10 mins of the boiler starting up, then you won't...
Replies
3
Views
279
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock