Discuss Viessmann Vitodens 200-W Problems in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Messages
18
I have two Vitodens 200-W system boilers connected via a low loss header. They are about 7 years old and have run perfectly since they were first installed until now. They were installed as part of a whole house re-plumb and have had Fernox MB-1 Heating Protector in the circuit since day one.

One still works fine, but one keeps overheating with either an F2 or an F3 error. When they were recently serviced the plumber replaced the flame sensors and the spark ignition probes on both boilers, but that didn't solve the problem. His next suggestion was to start replacing parts until he figures out what the problem is, but given the cost of Viessmann parts, I wasn't keen on that idea, so I have tried to go as far as I can myself without touching any of the gas related parts.

I have flushed through the heat exchanger with water from a garden hose and got a small amount of magnetite out, but it seemed to be flowing freely. I removed the directional control valve (which isn't used because of the low loss header) and found it was completely caked in a hard shiny black deposit which took a lot of effort to break up and remove from the rubber. I have swapped the pumps over between the two boilers in case the pump was faulty, but the problem has remained. I don't think I can do anything more without having to disturb the gas side which I know is illegal.

When I fire up the boiler it sounds like a kettle boiling. The burner quickly regulates down from full output to low (based on the fan speed) but the temperature on the screen on the front of the boiler keeps rising until it his 92C when it cuts off. The pump keeps running and the temperature gradually comes down until it reaches 62C when it ignites and the same happens again. Every so often it goes over 100C and then trips with an F2 or F3 error.

None of the local plumbers seem to be experienced with Viessmann domestic boilers, so does anyone have any ideas of what the problem could be or anything more I can try before I get the plumbers back?

One final thing - while I had the system depressurised yesterday, I also thought I would check the pressure in the expansion tanks on both the boilers. In both cases when I pressed a pressure gauge onto the Schrader valve I got fountains of water spewing out of the valve. I guess that means both the bladders have failed as there shouldn't be any water in there. Am I right?
 
Presumably you have no magnetic filter on the return to the boilers?

From the work you describe you have implemented, you have broken into the “room sealed” part of the boiler to access the heat exchanger. If so, the seals should be checked by a Gas Safe Registered engineer before you attempt to use the boiler.

Personally, I would not use any plumber / heating engineer who’s modus operandi is progressive part replacement. I am surprised that he / she did not start to strip down your working boiler to source parts on a trial and error basis.

F2 and F3 codes on Viessmann are generally a straightforward fix, but you will need a Gas Safe Engineer to implement it.

If your system is very dirty that needs to be addressed before you bring the boiler back into operation.

Viessman do a fixed price repair - but that may not be applicable if there has been no debris protection (serviced magnetic filter) fitted to the installation.
 
Get them to remove and replace the rubber tubes

As for expansion vessel no, no water is supposed to come out
 
Thanks for getting back to me.

Both boilers actually have their own individual Fernox TF-1 filters on the return from the low loss header and there is one on the return from the heating circuit the goes around the house.

Thanks for confirming the expansion vessel questions - I thought so.

I will contact Viessmann and see what they can offer in terms of a fixed price fix, and otherwise I'll replace the expansion vessels and then get a Gas Safe plumber to replace the rubber tubes and re-check the seals.
 
There is a black rubber looking tube at the back between the pump and the back of the heat exchanger, with an automatic air vent half way along it.

It is hard and not flexible, so I don't know if it's rubber coated copper, or if it's rubber that's gone hard, but they is definitely one rubber type tube at the back (not including the condensate drain).
 
the early 200s did have them gasmk1

op dont squeeze them just get them replaced
 

Reply to Viessmann Vitodens 200-W Problems in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

D
hello! while saving up for a new plumbing and heating installation for my new one bedroom flat, i did a lot of research on different boilers and systems, sought some advice, and settled on a viessmann vitodens 050-w, seems to offer a lot in terms of features and reliability, offers good value...
Replies
51
Views
4K
Morning, I have a job later this week with the above , Viessmann Vitodens System boiler. It has a 4 pipe setup with internal diverter and at present there is a wireless thermostat/programmer controller in the hallway. Customer wants a Honeywell Evohome System and I just wondered if I can wire...
Replies
4
Views
497
A
Hi all, I have a viessmann vitoden 100 w boiler and we have had a three hour power cut this afternoon/ evening. The boiler switches on and the temp just goes down and then flashes up 0c. From what I can see this error code means blocked burner? The oven also will not ignite. I have tried to...
Replies
0
Views
340
Abbie S
A
M
Hi, Hopefully someone can throw some light on if this is a real issue or not. I have had this boiler for about 10 years, I noticed just recently that when the CH has been turned off that a couple of the rads closest to the boiler were slightly warm. When the boiler had demand to heat the DHW I...
Replies
1
Views
371
Hello! I have a large house, 20 radiators + UFH. Heated house area is about 350 m2. House is class B, it is written in the certificate that house requires 73 kWh(m2/year) for heating. I had my system fully upgraded last year, installed new Vitodens 200-W 49 kW (B2HA) model with Vitotronic 200...
Replies
71
Views
6K
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock