Search the forum,

Discuss Vaillant 838 operations in the Gas Engineers Forum area at PlumbersForums.net

Messages
27
Fitted a Vaillant 838 Eco Tech plus combination boiler to a property 6 weeks ago. all fine.
Customer called in to say that the boiler had locked out on F54 and F28. Reset did it again a few hours later, then been fine since.
I attended today to check a few thing:-
1. Gas pressure at the meter on Max was 20.5mbars
2. Gas pressure at meter on min was 22.5mbars
3. gas rate calculated at meter was bang on 38.5kw
4. pressure on max at the boiler was 13mbar. Working at the test point at the side/top of the gas valve. the book states that the operating band is 13 to 22mbars.

The pipe run is in 22mm to the boiler is minimal, no more than 6mtrs

I was a little surprised that the pressure at the valve was 13mbars since the gas rate was a little over allowing for errors.

if this becomes an issue ( this is the only time it has done it) I can imagine Vaillant are going to say to increase the pipe size?

Apart from a drop in supply pressure from the supplier has anyone else experienced this?

Since it is a Sunday morning please be nice.
 
I think Scott means shale often there can be some debris in the gas supply worth checking , always cut a a test point in before the gas valve and 38 kw always a 28mm supply . Kop
 
THANKS FOR THE ADVICE. i did it at 22mm since it was such a small run, but if it plays up again ill run it in 28mm.

in all honesty i forgot to do the external test point. I normally now fit the Vogue boilers which have them in the valve itself which is much better.
thanks for the reply
 

Reply to Vaillant 838 operations in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
306
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock