I'm going to replace my hot water cylinder with as close as I can to like for like. Replacing as it doesn't have an immersion heater.

It's a copper vertical 140Litre tank in an indirect vented system and the inlets and outlets seem pretty standard, except it has an outlet for the shower that's on the side of the cylinder and about 200mm below the top. The pipe to the shower has a valve quite close to the cylinder and then turns from horizontal to vertically down. The main outlet from the top of the cylinder has a bend 300mm above the cylinder then a short horizontal run into a Tee, that sends one pipe up to the header tank and the other down to the hot water system.

I've not been able to find a cylinder with an outlet on the side so am wondering if it would be OK to feed the shower from the top outlet by installing an additional tee in the horizontal section of pipe that is fed by the main outlet, and send the shower feed down and through a valve please?

Also, what's the reason for a dedicated shower feed on the existing cylinder please?

Thanks
 
Last edited:
The dedicated shower feed stops the shower from being starved of hot if another hot outlet is used- this is less of a worry if the shower valve is thermostatic. On a gravity system a non-thermostatic valve offers better flow rates, so changing to thermostatic can result in an unacceptable shower, but a non-thermostatic valve is subject to temperature fluctuations unless a dedicated feed is used.

The other point of a side outlet for shower hot is to provide an air free supply to a pump - this is very important but can be achieved in other ways too.

So wether you need this dedicated supply depends on if your shower has a pump, and if it’s thermostatic.

The side supply can be replicated by the addition of an Essex flange to your new cylinder (one cuts a hole in the cylinder and retro fits the flange, but tricky to do ) - then all your pipework can remain unaltered.

Alternatively Gledhill will add any number of tappings to a cylinder in the positions/sizes/threads of your choice, usually a short lead time but maybe longer due to Covid? This is an excellent service and not too costly - potentially saves you a lot of tome and fittings on the install and makes it a lot easier.
 
I'm going to replace my hot water cylinder with as close as I can to like for like. Replacing as it doesn't have an immersion heater.

It's a copper vertical 140Litre tank in an indirect vented system and the inlets and outlets seem pretty standard, except it has an outlet for the shower that's on the side of the cylinder and about 200mm below the top. The pipe to the shower has a valve quite close to the cylinder and then turns from horizontal to vertically down. The main outlet from the top of the cylinder has a bend 300mm above the cylinder then a short horizontal run into a Tee, that sends one pipe up to the header tank and the other down to the hot water system.

I've not been able to find a cylinder with an outlet on the side so am wondering if it would be OK to feed the shower from the top outlet by installing an additional tee in the horizontal section of pipe that is fed by the main outlet, and send the shower feed down and through a valve please?

Also, what's the reason for a dedicated shower feed on the existing cylinder please?

Thanks
Here's a couple of photo of mine, IMI circa 1994

IMG_20200620_090652351.jpg
IMG_20200620_090715179.jpg


15mm shower is the top one on the side.

Think my shower is non thermo, but I would not worry about that, just don't run the bath at same time . . . Depends on how many in the house though.

Cheers,

Roy
 
Thanks for your helpful replies Ben-gee and Gasmk1.
It's a gravity pressurised system with a thermostatic shower.
The path of least risk is, I think, to use a Surrey flange. I don't mind modifying the pipework to suit.
Edited to add, thanks Roy as well. I don't wish to have to manage the use of the various hot water outlets. That would be a step in the wrong direction.
 

Reply to Replacement hot water cylinder query in the USA area at PlumbersForums.net

Similar plumbing topics

Hi, I'm in my new build 2 years and the shower pump has died. I have an air to water unit downstairs is in the utility which I've been told is unvented and pressurised. The cold water feed into this cylinder is from the attic tank, not the mains as I turned off the mains stopcock to see if hot...
Replies
6
Views
160
I need to change my shower mixer and I have a unvented hot water cylinder. Is it sufficient to turn off the mains? Do I need to drain the cylinder? Thanks
Replies
0
Views
341
Hi There was no shut off valve on the tank feed to the hot water cylinder, and I needed to move a couple of hot water pipes, so I shut off the mains water, turned boiler off (Remeha avanta) and opened the hot kitchen tap to drain the cylinder. After doing the work etc, Everything up and...
Replies
4
Views
213
I have a vented hot-water cylinder that was installed when the house was built - 38 years ago! It has a header tank in the loft and the cylinder is located directly above the ceiling of a new and expensive kitchen. It does not leak and causes no obvious problems. Should it be replaced? Advice...
Replies
4
Views
510
I recently installed new hot and cold feeds to a new downstairs cloakroom. After refilling the system the hot taps were all dribbling, spluttering and showing signs of an air lock. I attached cold mains to a hot tap and left it running for 15 minutes, while opening up each hot tap. They all...
Replies
2
Views
501
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock