Jacko

Gas Engineer
Messages
58
Hello guys advice needed.
Combi boiler fires up burner lights comes on for about 20 seconds and then goes off, this is followed by a L1 fault... in ch and hw mode.
System pressure ok
Flow thermistor 14kohms at room temp
Return thermistor 14kohms at room temp.
Pump seems to operate, can only check by touching it as it is an A rated pump with no front screw.
Flow return valves areopened the boiler flow pipe within the combustionchamber doesnt really get hot.
When boiler operates itseems to modulate up and then down before shuttingoff with the L1 fault.. I am thinking possible week pump but as it’s nearly£300 I need to be sure....any suggestions
 
Hello guys advice needed.
Combi boiler fires up burner lights comes on for about 20 seconds and then goes off, this is followed by a L1 fault... in ch and hw mode.
System pressure ok
Flow thermistor 14kohms at room temp
Return thermistor 14kohms at room temp.
Pump seems to operate, can only check by touching it as it is an A rated pump with no front screw.
Flow return valves areopened the boiler flow pipe within the combustionchamber doesnt really get hot.
When boiler operates itseems to modulate up and then down before shuttingoff with the L1 fault.. I am thinking possible week pump but as it’s nearly£300 I need to be sure....any suggestions

Boiler fixes can't be discussed on the open forums on this site. You need to contact @ShaunCorbs with details of your Gas Safe registration number for access to the closed forums.

If you are not GSR yourself, all we can advise you to do is put the covers back on your boiler and employ a qualified person to investigate and repair.
 
Hello guys, thanks for your help, will try the pump. Sorry for using the wrong forum luckily Shaun helps me out on that note.

Post once more
 
Pump operates fine, can only think of a restriction in the main heat exchanger....Ideal tech support also state the same, they advise removal of main heat exchanger and a clean out!!!!. customer advised to call out Ideal on a one off fixed fee call out.
 
I took the pump out and tested it, it worked well. Apparently you can stick a thin screwdriver in the middle of it, push the screw driver in and check to see if the pump spins...
If the customer goes with Ideal I will find out the fix and post it.
 
I took the pump out and tested it, it worked well. Apparently you can stick a thin screwdriver in the middle of it, push the screw driver in and check to see if the pump spins...
If the customer goes with Ideal I will find out the fix and post it.

Spinning and pushing water around a system are too different things .
 

Reply to Ideal Independent C30 in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I just installed second zone onto my ideal independent c35 original I had one hive thermostat now I added two two port valves ( with Bypass) and two hive thermostat V3 it wired into a wiring centre looking at the wiring on the boiler shall I put back the room stat/ timer loop back in as...
Replies
4
Views
418
Hello friends - I really struggle to understand my heating and hot water system I posted my question on Diynot but it ended up being five pages and couldnt get to the bottom of it and I thought worth asking the elders on here for their view - Hot water temp is 40 Degrees - Ideal Mexico 2...
Replies
10
Views
680
Do people with this type of mixed flow temperature control have any problems with achieving the required manifold flow temperature? The one below I think is similar to the TIO Mixing unit. In the unit below, the hot (boiler) water enters from the bottom left, red arrow, up through the "mixing...
Replies
3
Views
515
Hi Fitted a new out the box’s boiler today. It worked for 30 minutes. Then stoped and went to fault codes 2965 B Flow temperature too high ▶ System is not filled with water. ▶ No water flow,because CH system is closed. ▶No water flow, because pump is not operating correctly. ▶ Check flow...
Replies
6
Views
960
Hi Folks, I have a challenge with a Main Eco Elite 30 Combi which is short cycling on the CH. Water works fine. As soon as you have call for heat, the boiler fires up, modulates, but jumps very quickly (about 30 seconds or so from 40'ish all the way to 70, burner disengages putting it the...
Replies
6
Views
368