Messages
12
Have traditional vented indirect system, in my case F&E tank base same level as large tank, so top level of f&e tank is lower, F&E tank overflows/steady trickle, maybe one bucket every 3 hours, also somewhat brownish water (water from taps crystal clear), guess it is coil, or could system be too hot (at one stage hot water was VERY hot), any suggestion?
 
Sounds more like the vent on the f&e tank is pumping over, whenever I’ve come across split cylinder coils you get iron oxide particles coming out your hot water taps/discoloured water. Could be your hw zone valve microswitch sticking causing the boiler an pump to be on with nowhere to circulate then ending up pumping over via the open vent & slightly passing through the hw zone valve to heat the coil giving you hotter water. It’s just a guess mate given you said hot water was very hot, H section could also be restricted causing f&e tank to overfill.
 
Sounds more like the vent on the f&e tank is pumping over, whenever I’ve come across split cylinder coils you get iron oxide particles coming out your hot water taps/discoloured water. Could be your hw zone valve microswitch sticking causing the boiler an pump to be on with nowhere to circulate then ending up pumping over via the open vent & slightly passing through the hw zone valve to heat the coil giving you hotter water. It’s just a guess mate given you said hot water was very hot, H section could also be restricted causing f&e tank to overfill.
Thanks, very detailed, pity you are not a plumber in my area (N20), even as a lay person I would have thought that if there is a hole in the coil it lets water from heating circuit into the cylinder and then tap water is discolored (Though somewhere I read it could be the other way, depending on relative positions of small and large tank, but somehow cannot imagine water FROM cylinder goes into heating circuit, would at some stage be overfull, though maybe that is why overflow goes into f&e tank).
Also worth mentioning, water goes into f&e tank not from the vent pipe hanging over the edge and freely visible, it must come from the opening at the bottom level...any more ideas? drives me mad, worse than the Rubik cube!
 

Reply to F&E tank overflow - brownish water - tap water crystal clear in the Canada area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
250
I have a plumber coming tomorrow to change a cartridge on a badly dripping tap on my bathroom mixer unit. There is no separate isolating valve for this tap so I'll have to close the stopcock. I tried closing it today but it won't go absolutely 100% closed and there is still a very slight flow...
Replies
1
Views
207
Hi, basic question, any insight much appreciated. Looking to have an outdoor tap in my front porch fed from 15mm pex coming up from suspended floor. Pic 1 is inside porch, pex temporarily clipped to give an idea of pipe placement (ignore shoddy blockwork of booted cowboy builder!), Pic 2 is...
Replies
6
Views
199
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
2
Views
148
The fittings below are for a mixer bar attached to a self contained shower. i.e not a wall. The attaching screws have snapped. I could get two new brackets, dismantle that existing one and start again or I could try and re attach via those screws, removing the broken ones from the plate and wall...
Replies
0
Views
108
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock