I have a glow worm 18sxi, in having a few problems and my insurance are saying its because it doesnt have a constant live so they wont cover the problem as it was installed this way 13 years ago. So does it have to have a constant live?
Discuss Does a Glow worm 18sxi need a constant live in the USA area at PlumbersForums.net
I have a glow worm 18sxi, in having a few problems and my insurance are saying its because it doesnt have a constant live so they wont cover the problem as it was installed this way 13 years ago. So does it have to have a constant live?
I'm not sure this helps me, my boiler isnt live unless it has a demand to heat the hot water for the tank or heating.The installation instructions for the 18sxi clearly state that the mains must be maintained
uninterrupted at all times.
From the installation manual:
"The mains electrical supply must be maintained at all times in
order to provide domestic hot water.
Do not interrupt the mains supply with a time switch or
programme"
Hope this help you.
That's great thank you, the insurance company are saying it could be a faulty programmer or the fact it hasnt got a permanent live that is causing the boiler to ignore the programmer when there is no demand.I would suggest for things like pump over run a permanent live should be there.