Could you explain what natural draught r/s means?
Fanned draught r/s?
Natural draught o/f?
Fanned draught o/f?

Ps. Flues are my weak point so any relevant information would be helpful.
 
Flue Categories
A, B, C - flueless, open flues, room sealed

1st digit - denotes method of arranging discharge of combustion
1 - with draught diverter
2 - with out draught diverter

2nd digit - denotes flue draught method
1 - natural draught
2 - fan downstream of heat exchanger
3 - fan upstream of heat exchanger
4 - fan downstream of draught diverter

Open-flued Systems
Open-flued systems


Category B

Balanced Compartments

Self-closing and draught proof door
Switch fitted to the door that turns off the appliance if the door is opened
Door shall not open into a bathroom
If over 12.7kW shall not open into bedroom
Keep closed notice on the door
No other ventilation into compartment
4 parts of an open flued appliance

Primary Flue

Part of the appliance
Creates the initial flue pull to clear the products of combustion
Draught Diverter
Diverts any down draught from the burner
Allows dilution of flue products
Breaks any excessive pull on the flue
Usually part of the appliance

Secondary Flue
Horizontal runs must be avoided
Bend minimum 45°
Keep internal where possible
Minimum 600mm vertical rise to the first bend
Cross sectional area of flue must be at least equal to that of the appliance

Terminal
Stop birds nesting or leaves entering the flue
Minimise down draught
Help the flue gases discharge
Terminals are not required for chimneys with a flue size greater than 170mm if no nesting will occur

Vertex Flue
Air supply taken from the roof space
Draught Diverter min height is 300mm above the loft insulation
The flue above the Draught Diverter must run for 600mm before any bend

Room-sealed Flue Systems

Room-sealed Flue Systems

Category C
Balanced (natural draught) flue
Fan-assisted flues
negative pressure within the casing
positive pressure within the casing
Termination options
Vertical room-sealed flue termination

Vertical room-sealed flue termination

all on google but you should have all this in your viper / niceic book
 
Flue Categories
A, B, C - flueless, open flues, room sealed

1st digit - denotes method of arranging discharge of combustion
1 - with draught diverter
2 - with out draught diverter

2nd digit - denotes flue draught method
1 - natural draught
2 - fan downstream of heat exchanger
3 - fan upstream of heat exchanger
4 - fan downstream of draught diverter

Open-flued Systems
Open-flued systems


Category B

Balanced Compartments

Self-closing and draught proof door
Switch fitted to the door that turns off the appliance if the door is opened
Door shall not open into a bathroom
If over 12.7kW shall not open into bedroom
Keep closed notice on the door
No other ventilation into compartment
4 parts of an open flued appliance

Primary Flue

Part of the appliance
Creates the initial flue pull to clear the products of combustion
Draught Diverter
Diverts any down draught from the burner
Allows dilution of flue products
Breaks any excessive pull on the flue
Usually part of the appliance

Secondary Flue
Horizontal runs must be avoided
Bend minimum 45°
Keep internal where possible
Minimum 600mm vertical rise to the first bend
Cross sectional area of flue must be at least equal to that of the appliance

Terminal
Stop birds nesting or leaves entering the flue
Minimise down draught
Help the flue gases discharge
Terminals are not required for chimneys with a flue size greater than 170mm if no nesting will occur

Vertex Flue
Air supply taken from the roof space
Draught Diverter min height is 300mm above the loft insulation
The flue above the Draught Diverter must run for 600mm before any bend

Room-sealed Flue Systems

Room-sealed Flue Systems

Category C
Balanced (natural draught) flue
Fan-assisted flues
negative pressure within the casing
positive pressure within the casing
Termination options
Vertical room-sealed flue termination

Vertical room-sealed flue termination

all on google but you should have all this in your viper / niceic book
Thank you for your help! Highly appreciated
[automerge]1591717469[/automerge]
Flue Categories
A, B, C - flueless, open flues, room sealed

1st digit - denotes method of arranging discharge of combustion
1 - with draught diverter
2 - with out draught diverter

2nd digit - denotes flue draught method
1 - natural draught
2 - fan downstream of heat exchanger
3 - fan upstream of heat exchanger
4 - fan downstream of draught diverter

Open-flued Systems
Open-flued systems


Category B

Balanced Compartments

Self-closing and draught proof door
Switch fitted to the door that turns off the appliance if the door is opened
Door shall not open into a bathroom
If over 12.7kW shall not open into bedroom
Keep closed notice on the door
No other ventilation into compartment
4 parts of an open flued appliance

Primary Flue

Part of the appliance
Creates the initial flue pull to clear the products of combustion
Draught Diverter
Diverts any down draught from the burner
Allows dilution of flue products
Breaks any excessive pull on the flue
Usually part of the appliance

Secondary Flue
Horizontal runs must be avoided
Bend minimum 45°
Keep internal where possible
Minimum 600mm vertical rise to the first bend
Cross sectional area of flue must be at least equal to that of the appliance

Terminal
Stop birds nesting or leaves entering the flue
Minimise down draught
Help the flue gases discharge
Terminals are not required for chimneys with a flue size greater than 170mm if no nesting will occur

Vertex Flue
Air supply taken from the roof space
Draught Diverter min height is 300mm above the loft insulation
The flue above the Draught Diverter must run for 600mm before any bend

Room-sealed Flue Systems

Room-sealed Flue Systems

Category C
Balanced (natural draught) flue
Fan-assisted flues
negative pressure within the casing
positive pressure within the casing
Termination options
Vertical room-sealed flue termination

Vertical room-sealed flue termination

all on google but you should have all this in your viper / niceic book
Could you please provide the link to this page?
 
Last edited:
type into google flue types
 

Reply to Could someone please help me with this? in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

Hi guys. I'm trying to identify a toilet model before ordering a seat for a customer. I went to what used to be a Roca stockist (they no longer are) and one of the guys there reckoned it might be "The Gap". I went to the new stockist and the guy there disagreed it was "The Gap" and that he'd...
Replies
2
Views
102
  • Sticky
Morning to any Australians lurking around! Register its free, then message me, I'll sort your account out for you. We will need a moderator from each main country too. I'll post this in the Australian forum now.
Replies
0
Views
49
Hi, basic question, any insight much appreciated. Looking to have an outdoor tap in my front porch fed from 15mm pex coming up from suspended floor. Pic 1 is inside porch, pex temporarily clipped to give an idea of pipe placement (ignore shoddy blockwork of booted cowboy builder!), Pic 2 is...
Replies
6
Views
187
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock