Hi - first post here

Trying to resolve an issue with our system at the moment. We have a Potterton Suprima boiler with a Sunvic 207 XLS programmer. I’m only able to get CH to work when HW is active. There is no HW off wiring into the programmer which I imagine could be the issue after doing some research.

However, something that confuses me... when I send a call for CH only this activates the micro switch in the three port valve and turns the spindle. So far so good.... but it doesn’t fire up the boiler.

Just wondered if this would be a wiring issue (due to not having a HW off lead on the programmer) or whether this could be a physical issue with the valve itself.

I’m a total novice but have been studying the Y-Plan and looking at our setup for a number of hours! I imagine a HW off wire could solve the problem but obviously it’s a big job running wires from the wiring unit in the airing cupboard upstairs to the programmer next to the boiler.

I’m about to get a Nest installed so wanted to resolve this before going ahead with that if I could. Would a Nest make any difference to the issue I have if I were to go ahead with the current way of working (having to put HW on when I want CH)

Any advice or thoughts welcomed.
Many thanks
 
Could be a port valve issue eg not moving all the way to heating so the micro switch isn't contacted
 
I would start testing you any good at elec fault finding ?
 
Check on the back of the clock. Is the top dips witch set to gravity. If it is you could have had an old gravity system at some point and whoever installed the suprima set it up like this to save running a new cable
 
It may be a W-plan as opposed to a Y-plan. That is Hot water priority. If it is, you'll need to completely wire the system to Y-plan. It's not as daunting as you would think. Find a competent engineer who can wire if you're not sure.
 
Been mapping out the wiring on the system tonight and finally got to grips with it all. It’s a Y-Plan and I’ve found a blue wire tucked behind the programmer which isn’t connected to anything and a further blue wire in the junction box upstairs, also not connected to anything. Will test it prior to connecting tomorrow but I’m 90% certain that it’s the HW off (or at least I can use it for that)

Therefore I’ll be installing the Nest heat link where the original programmer was but then I need to work out how to connect T1 and T2 on the Nest stat to the heat link - I’ll save that for another post!!
 
You would be better off installing the heat link next to wiring center and disconnecting the old programmer. If the blue turns out it’s not the same cable either end then you could install a relay to act the same as HW OFF.
 
All sorted now, thanks all for the advice and pointers

The blue wire was indeed the HW off and when I connected this up to the existing programmer the call for heat alone worked as expected. This was a big result for me!

I then intended on putting the Nest Heat Link next to the wiring center so I could use the original room thermostat wiring for T1 and T2 on the Nest.

However.... I came to find that all my live connections are located next to the boiler and fuse spare downstairs. So I’ve ended up putting the Heat Link where the programmer was and I’m using the Nest thermostat wirelessly in the living room. Probably a better location for it really but not what I originally intended.

All up and running well though which is great.
 

Reply to CH only works when HW on (no HW off on programmer) in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi All, Hope somebody can help :) I have a vented HW system with a pressurised Ch system but got bit of a annoying issue, when the hot water comes on all seems ok then after about 15/20 mins i started to hear a trickling noise from hw cylinder which i can also hear in the boiler. The central...
Replies
3
Views
459
Hello. I've just replaced our old Potterton EP2 CH controller with a Drayton Wiser HubR (& peripherals). The old backing plate wasn't compatible with the new universal one, but the wiring was pretty close AFAICT (N, L, 1, 3 & 4 connected) .When I first powered it up but didn't have any TRVs...
Replies
1
Views
252
I've just noticed that with the CH programmer either selected off or timed off, the CH can still be controlled on/off at the room thermostat. HW is controlled by the same programmer and is operating normally. System is a pumped Y plan. I take it the programmer is fubar? Anything I can do to...
Replies
6
Views
732
Hi, would appreciate any thoughts on the below. I have an almost 10yr old Ferroli Modena 32S HE system boiler. (I am aware of their reputation! ) 2 weeks ago HW went lukewarm. When HW was called, the rads came on. The cylinder motorised valve has been replaced today, but it's not fixed the...
Replies
3
Views
491
  • Question
I have a problem where my HW heats only when my CH is not on. When both are on only CH works. I have insurance for the boiler and heating, but not covered for just heating issues (should have read the small print). I have changed the mid port valve actuator and the programmer (Drayton for...
Replies
8
Views
765
Deleted member 120897
D
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock