Our Boiler is a Baxi neta-tec combi boiler,installed 2011 and serviced by the same gas safe firm every year.It has not had the central heating run until recently.When this is called for the boiler goes through the motions of trying to light ,gets what i would call a soft flame and then goes out.This cycle continues until the flame failure alarm ,code 128,occurs.The reset button is pressed a few times,the boiler resets and wil light (not on the first attempt but will light)
When lit succesfully,there is a noise as the flame gets stronger(it sounds healthy).Could this be what i would call the high flame
The hot water side works fine
Parts renewd by the gas firm so are:-
Pcb board
Flame sensing electrode
Flow return sender (pt no :-T-o-d s) not sure of the part description no taken from part
Another sensor (pt no:-ontoil-6609-l105-1115 ab)not sure of the part description no taken from part
Leads to these sensord have been replaced also
The gas valve has been exchanged with another then ruled out and replaced with the original

The boiler was lit on heating via the remote control device and cut out.The remote control device was moved to a cooler room and after some time cooled down ,called for heat and the boiler lit with a healthy sounding strong noise .
The remote control was turned down to a low temp for the evening and in the morning was turned up,calling for heat but the boiler failed again with the error code 128,the reset button pressed and it eventually started.
Has any one any experiance of what could be the cause,maybe something sticking after not being used for several months
Thanks for any suggestions
regards
 
Get baxi in to do a one off repair.
Gasmk1,
thank you for youre reply.I have already been in touch with Baxi snd they say they would send some one and i must take out their insurance policy that will cover me for breakdowns for 12 months.They did not say what would be covered.That would be approx £350 + the cost of parts and labour so far but will bear it in mind
 
Gasmk1,
thank you for youre reply.I have already been in touch with Baxi snd they say they would send some one and i must take out their insurance policy that will cover me for breakdowns for 12 months.They did not say what would be covered.That would be approx £350 + the cost of parts and labour so far but will bear it in mind

nooo they do another service which is a fixed price repair normally around the 250/270 mark
 
I think the gas valve will probably need setting up. If it fires up and then goes off then I’m assuming when it modulates it fails as a result it knocks off.
AMGasServices
Thanks for youre reply.When you say set up the gas valve do you mean check the pressure.Our chap has replaced the gas valve,a straight swop for the one in use,changed them back again and said that he didnt think it was the gas valve.Although when connecting it back he plugged in an electrical connection on the gas valve and said the solenoid was noisy
Thanks all the same though
I think the gas valve will probably need setting up. If it fires up and then goes off then I’m assuming when it modulates it fails as a result it knocks off.
 
AMGasServices
Thanks for youre reply.When you say set up the gas valve do you mean check the pressure.Our chap has replaced the gas valve,a straight swop for the one in use,changed them back again and said that he didnt think it was the gas valve.Although when connecting it back he plugged in an electrical connection on the gas valve and said the solenoid was noisy
Thanks all the same though

You can’t just swap a gas valve like for like these day it requires setting up.

I’m pretty much convinced the gas valve is causing your issue. The gas valve has three different modes I can’t remember them and they would need to be check and set up in accordance with the Manufacture Instructions.

It’s a really time consuming process eventually your issue with be sorted.
 
You can’t just swap a gas valve like for like these day it requires setting up.

I’m pretty much convinced the gas valve is causing your issue. The gas valve has three different modes I can’t remember them and they would need to be check and set up in accordance with the Manufacture Instructions.

It’s a really time consuming process eventually your issue with be sorted.
Thanks for the reply
Found it in the book,combustion and calibration,it starts combustion should be *** at all 3 fan speeds,then goes on to calibration function and adjusting the co2.Is this what you mean
The trouble shooting flow chart also said to renew the heating flow /return sensor.
Thats going to be done today
Did try to past the page in but couldnt hence the short description and length of time to reply
 
Thanks for the reply
Found it in the book,combustion and calibration,it starts combustion should be *** at all 3 fan speeds,then goes on to calibration function and adjusting the co2.Is this what you mean
The trouble shooting flow chart also said to renew the heating flow /return sensor.
Thats going to be done today
Did try to past the page in but couldnt hence the short description and length of time to reply

Yes it’s something like that but an ordinary person can’t set it up it has to be set up using a gas flue analyser.

I would get the sensors changed just yet.

I think your have practically rebuilt the boiler from inside. It would have been cheaper to get a fixed price repair from Baxi.
 
It does sound like the boiler isn’t modulating correctly. Either it needs adjusting or you haven’t used the correct o-ring for that boiler as the o-ring is restricted to allow a set amount of gas through depending on boiler output.
 
It does sound like the boiler isn’t modulating correctly. Either it needs adjusting or you haven’t used the correct o-ring for that boiler as the o-ring is restricted to allow a set amount of gas through depending on boiler output.
Our chap came today,after a promise to be here on Mon,Tues and Wed and set up the gas valve,still no good.Tested the sensors,now thinks it could be the gas valve.
Where does this o-ring fit as one hasnt been changed.Could it be perished
Thanks
 
Our chap came today,after a promise to be here on Mon,Tues and Wed and set up the gas valve,still no good.Tested the sensors,now thinks it could be the gas valve.
Where does this o-ring fit as one hasnt been changed.Could it be perished
Thanks
Thanks for all the replies and advice.
Baxi called and calibrated the gas valve,started the boiler then stopped it and said it sounded as if the gas press was slightly high . Checked the RDS stick by plugging something into the usb port at the front and said it was ok but replaced it anyway
Another machine, a gas analyser ?, was connected to the gas valve and to the flue


Recalibrated and gas press lowered and seems to be ok so far
Again thanks for all the help and advice
 
Baxi probably updated the software via the USB port at the front of the boiler.

It’s good to hear your issues been solved.

Thanks for all the replies and advice.
Baxi called and calibrated the gas valve,started the boiler then stopped it and said it sounded as if the gas press was slightly high . Checked the RDS stick by plugging something into the usb port at the front and said it was ok but replaced it anyway
Another machine, a gas analyser ?, was connected to the gas valve and to the flue


Recalibrated and gas press lowered and seems to be ok so far
Again thanks for all the help and advice
 

Reply to Baxi Neta-tec works on water but intermittant on ch heating in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
175
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
3
Views
212
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
256
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
185
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock